    cylinder and solenoid help
    #1
    mrdonenzone is offline Crypt Keeper
    Join Date
    May 2011
    Posts
    109


    Hey everyone, I assembled my trash can trauma prop today, and when I turned on the air compressor, the cylinder went up (without me activating the solenoid) and then would not go back down until I turned off the compressor. The solenoid made a clicking sound when activated by the picaboo, but nothing happened. At this point, I will buy a kit or anything to get it working. I have a professional haunt planned this year.
    Creepy.
    Reply With Quote
     

  2. Collapse Details
    #2
    Dark lord's Avatar
    Dark lord is offline HELLoween Ubber Lord
    Join Date
    Jan 2007
    Location
    Hell's pit - So. San Francisco,CA
    Posts
    2,177
    A little more info on the cyl ( single with spring return or double action ) & solenoid ( 2, 3, 4 or 5 way valve )....?
    When you look in the mirror at midnight,....what looks back at you.........
    Reply With Quote
     

  3. Collapse Details
    #3
    mrdonenzone is offline Crypt Keeper
    Join Date
    May 2011
    Posts
    109
    double acting cylinder, 12v 5 valve solenoid
    Creepy.
    Reply With Quote
     

  4. Collapse Details
    #4
    DangersAhead's Avatar
    DangersAhead is offline Werewolf
    Join Date
    Sep 2010
    Location
    Port Huron Mi
    Posts
    70
    is it possible the picaboo is on normally closed instead of normally open or possible switching the airlines. what type of cylider do u have
    Reply With Quote
     

  5. Collapse Details
    #5
    mrdonenzone is offline Crypt Keeper
    Join Date
    May 2011
    Posts
    109
    i checked and it is not. I switched the airlines both ways, and neither worked. I think im going to buy a new solenoid. It is a double acting cylinder.
    Creepy.
    Reply With Quote
     

  6. Collapse Details
    #6
    Industen's Avatar
    Industen is offline The Great Pumpkin
    Join Date
    Oct 2006
    Posts
    754
    Reply With Quote
     

  7. Collapse Details
    #7
    Industen's Avatar
    Industen is offline The Great Pumpkin
    Join Date
    Oct 2006
    Posts
    754
    If you cylinder raises..or extends the hoses should be switched around. The A and B on the solenoid should match the inputs on your solenoid. Make sure your solenoid is correct. A 5 way has 2 exhausts, 2 inputs, and one main line where the compressor goes in.

    Usually

    A and B are for the cylinders
    The bottom middle is the main (P)
    on the left and right of this main are the exhausts (R and S)
    Reply With Quote
     

  8. Collapse Details
    #8
    mrdonenzone is offline Crypt Keeper
    Join Date
    May 2011
    Posts
    109
    is it possible that my solenoid has a broken valve?
    Creepy.
    Reply With Quote
     

  9. Collapse Details
    #9
    Industen's Avatar
    Industen is offline The Great Pumpkin
    Join Date
    Oct 2006
    Posts
    754
    The relay could be defective, although it usually doesn't happen very often. Can you take a picture of the solenoid and post it here. Do you have a 12v power supply attached to it?
    Reply With Quote
     

  10. Collapse Details
    #10
    mrdonenzone is offline Crypt Keeper
    Join Date
    May 2011
    Posts
    109
    yes and yes, how do I post a picture? Do i upload it to photobucket
    Creepy.
    Reply With Quote
     